Fuji running at startup

Posted: Fri Sep 28, 2018 11:53 am
by om_tech_support_KR
Q: I am using a Fuji inverter on a conveyor and I want it to start running on power up without having to press the run button.

A: For this you would have to change 2 codes: change code F02 “Operation Method” from 2: “RUN/STOP keys on keypad (forward)” to 1: “Terminal command FWD or REV”. Then you will have to wire the FWD or REV input to the CM input to have it run in the desired direction.

F code.PNG
F code.PNG (190.86 KiB) Viewed 381 times


The other code is H96 “STOP Key Priority/Star Check Function”. It would need to be changed from 3 to 1 so the VFD won’t alarm out with Er6 when started.

H code.PNG
H code.PNG (164.4 KiB) Viewed 381 times


Inputs.PNG
Inputs.PNG (109.5 KiB) Viewed 381 times