Hi
I am using BLV R series drive, how to take speed output in this?

om_tech_support_KR
Posts: 142
Joined: Thu Jan 11, 2018 3:03 pm

Re: BLV R

Post by om_tech_support_KR » Thu May 12, 2022 9:07 am

Hello,

To read the speed you will have to read the Actual velocity register referenced on page 273 of the manual via RS-485 Modbus RTU. Note this will give you the speed at the moment its read it will not continuously update. From the outputs you can look at the VA or ZV parameters. VA turns ON when the operating velocity reaches the target velocity. This is referenced on page 176. ZV turns ON when the actual velocity is equal to or less than the "ZV detection speed range" parameter with the velocity 0 as a center. This is referenced on page 177.

https://www.orientalmotor.com/products/ ... f#page=273

Tridacsolution
Posts: 2
Joined: Wed May 11, 2022 11:40 pm

Re: BLV R

Post by Tridacsolution » Mon May 16, 2022 12:53 am

Hi

Thank you for the information,
is it possible to take position feedback in BLV-R Series?

om_tech_support_KR
Posts: 142
Joined: Thu Jan 11, 2018 3:03 pm

Re: BLV R

Post by om_tech_support_KR » Mon May 16, 2022 12:46 pm

Hello,

You can read the position feedback with the Actual position register also on page 273.