Search found 89 matches

by om_tech_support_KR
Mon Aug 10, 2020 12:29 pm
Forum: Speed Control Systems
Topic: BLV 200 & 400 Watts for AGV Application
Replies: 4
Views: 2202

Re: BLV 200 & 400 Watts for AGV Application

Hello, The 2 blink alarm is an overload alarm meaning a load exceeding the rated torque was applied to the motor for 5 seconds or more. You would have to decrease the load or try having the accel/decel rate at a higher value. In your case since it happens while doing a left turn you might have to tr...
by om_tech_support_KR
Tue Aug 04, 2020 8:40 am
Forum: Stepper Motors and Controls
Topic: Need help for Fx5U with AZ-KD via RS-485 PLC Programming
Replies: 1
Views: 49

Re: Need help for Fx5U with AZ-KD via RS-485 PLC Programming

Hello,

We do not have an example program for your specific PLC but we do have a general example in our manual. It starts on page 286 I will link it below so you can reference it.

https://www.orientalmotor.com/products/ ... 262-6E.pdf
by om_tech_support_KR
Thu Jul 09, 2020 7:09 am
Forum: Application Notes
Topic: Protection Options & Alarms Offered for Fan Products
Replies: 6
Views: 14759

Re: Protection Options & Alarms Offered for Fan Products

Hello, Correct you will need to supply external power supply up to 30 VDC to black and orange wires as these don't output any voltage. Below is a sample wiring diagram from another one of our drivers but it is also open collector type for the outputs. The outputs would be Y0 and Y1 there is a sample...
by om_tech_support_KR
Mon Jul 06, 2020 8:14 am
Forum: General Discussion
Topic: How to receive data through a EthernetIP>EtherCAT device from a PLC Controller
Replies: 3
Views: 335

Re: How to receive data through a EthernetIP>EtherCAT device from a PLC Controller

Hello, Unfortunately we don't have a tutorial on this or have a way to directly control the AZD3A-KED driver directly via EthernetIP. We do offer EthernetIP drivers but they are single axis drivers we don't offer a multi-axis driver. I will link it below note it uses different connection cables from...
by om_tech_support_KR
Thu Jul 02, 2020 10:52 am
Forum: Application Notes
Topic: Protection Options & Alarms Offered for Fan Products
Replies: 6
Views: 14759

Re: Protection Options & Alarms Offered for Fan Products

Hello, Correct you will have to supply voltage to the orange and black wires. To read the signal you will have to wire your PLC in series if you are sourcing power from a power supply and not your PLC. When an alarm is present you will read out the voltage you are inputting from your power source ei...
by om_tech_support_KR
Thu Jul 02, 2020 10:17 am
Forum: General Discussion
Topic: How to receive data through a EthernetIP>EtherCAT device from a PLC Controller
Replies: 3
Views: 335

Re: How to receive data through a EthernetIP>EtherCAT device from a PLC Controller

Hello, The MEXE02 software would mainly be used to change parameter and could also monitor some parameters. But you won't be able to send commands directly to the software from the PLC you will have to send them from your PLC to the driver. Then you will have to read data from the driver to the PLC ...
by om_tech_support_KR
Thu Jul 02, 2020 9:05 am
Forum: Speed Control Systems
Topic: 51K40RGN-C Speed-Control Motor wiring
Replies: 1
Views: 191

Re: 51K40RGN-C Speed-Control Motor wiring

Hello, Yes the wiring from the attachment is correct. You can check if the capacitor is not working by rotating the motor shaft while the motor is receiving power and if this get the motor started then it would mean the capacitor needs to be replaced. Also you can also check if the motor is receivin...
by om_tech_support_KR
Mon Jun 29, 2020 1:58 pm
Forum: Application Notes
Topic: Protection Options & Alarms Offered for Fan Products
Replies: 6
Views: 14759

Re: Protection Options & Alarms Offered for Fan Products

Hello, The diagram referenced would only be for the MRS14-TTM fan. The fan used in your kit is the MRS18-TTM. The alarm output would be open collector type so you will have to supply a voltage to it to read the output. You can use up to 30 VDC and the current will have to be limited to 15 mA with re...
by om_tech_support_KR
Thu Jun 25, 2020 2:01 pm
Forum: Stepper Motors and Controls
Topic: Data register modbus Rs485 input command
Replies: 8
Views: 587

Re: Data register modbus Rs485 input command

Hello,

For your step 3 when you write a decimal value 64 to 007Dh you will be turning on Bit6 which factory setting will be the FREE input which cuts power to the motor. If you want to run a Home sequence then you will have to write a decimal value 16 to 007Dh. This will turn on the Bit4 Home.
by om_tech_support_KR
Wed Jun 24, 2020 12:11 pm
Forum: Stepper Motors and Controls
Topic: Data register modbus Rs485 input command
Replies: 8
Views: 587

Re: Data register modbus Rs485 input command

Hello, Could you send me the query you are sending for the Home command? There is an example of this on page 251 of the manual I link below for reference. Also which register are you referring to by data register 64? Are you able to run any of the programmed positions or jog the motor via RS-485? ht...
by om_tech_support_KR
Tue Jun 23, 2020 12:15 pm
Forum: Stepper Motors and Controls
Topic: Data register modbus Rs485 input command
Replies: 8
Views: 587

Re: Data register modbus Rs485 input command

Hello,

Can you verify if you are writing a 0 before you send a command in the 007Dh register. If you don't write a 0 before the Home command and there is another command there it won't read correctly. Are you getting any alarms on the driver?
by om_tech_support_KR
Mon Jun 22, 2020 11:00 am
Forum: Stepper Motors and Controls
Topic: Data register modbus Rs485 input command
Replies: 8
Views: 587

Re: Data register modbus Rs485 input command

Hello,

What command are you writing to the 007Dh register? Also are you writing a 0 to it before you send the Home command? If you have the MEXE02 software you can use the Status I/O monitor to verify which inputs you are turning on with the RS485 commands.
by om_tech_support_KR
Tue Jun 09, 2020 11:07 am
Forum: Question of the Day
Topic: Load stopping torque
Replies: 1
Views: 249

Re: Load stopping torque

Hello, These links below can help in calculating the acceleration/deceleration torque. Also I will link our motor sizing tool that can calculate the torque, inertia and speed needed from the motor. https://blog.orientalmotor.com/motor-sizing-basics-part-3-acceleration-torque-and-rms-torque?hsCtaTrac...
by om_tech_support_KR
Mon Jun 01, 2020 2:09 pm
Forum: Stepper Motors and Controls
Topic: AR Series Stepper Motor Getting-7 time blinking alarm
Replies: 1
Views: 275

Re: AR Series Stepper Motor Getting-7 time blinking alarm

Hello, Thank you and hope you are safe as well. For the AR Flex type the 7 blink alarm has a couple of different alarms that can cause this. Are you able to look in the MEXE02 software to determine with alarm code it is? I will link the manual below the alarm codes start on page 143. https://www.ori...
by om_tech_support_KR
Fri May 08, 2020 2:04 pm
Forum: Stepper Motors and Controls
Topic: AZ Series Ethernet/IP driver - MicroLogix question
Replies: 1
Views: 343

Re: AZ Series Ethernet/IP driver - MicroLogix question

Hello, The Micro850 PLC hasn't been tested with our AZ Ethernet/IP drivers but you might be able to set it as a generic module and send implicit messages to our driver for control. The implicit communication section for our driver starts on page 83 of the link below. https://www.orientalmotor.com/pr...
by om_tech_support_KR
Wed Apr 08, 2020 10:24 am
Forum: Stepper Motors and Controls
Topic: SCX11 to Arduino
Replies: 1
Views: 383

Re: SCX11 to Arduino

Hello, When you save the program to the SCX11 controller you assign it a sequence number. If you want to run it off 1 input you can assign it sequence number 0 then when you turn on the START input it will run it. You will have to assign one of the I/O to START. This can be reference on page 129 in ...
by om_tech_support_KR
Mon Apr 06, 2020 11:12 am
Forum: Servo Motors & Controls
Topic: Allen Bradley 525 VFD used on 51K40VKEST
Replies: 1
Views: 570

Re: Allen Bradley 525 VFD used on 51K40VKEST

Hello, Your current VFD is rated for 380-480VAC this motor should only be used with VFDs rated for 240 VAC or lower. Using it with higher input voltage VFDs may cause the insulation of the motor windings to deteriorate, leading to damage to the motor. The compatible VFD we offer is a FUJI VFD but do...
by om_tech_support_KR
Mon Mar 09, 2020 8:20 am
Forum: Stepper Motors and Controls
Topic: AZ stepper start command to motion delay
Replies: 3
Views: 2740

Re: AZ stepper start command to motion delay

Hello, Since there are a couple of different alarm types for the 8 blink alarm I recommend using the MEXE02 software to narrow down the alarm code. If a sensor error its recommended to check the cables for any damage or you can try changing the cables from one of the systems that is working to see i...
by om_tech_support_KR
Mon Mar 09, 2020 7:13 am
Forum: Stepping Motors & Controls
Topic: Changing stepper motor direction by swapping wires?
Replies: 2
Views: 18263

Re: Changing stepper motor direction by swapping wires?

Hello, For the 10 lead to new polar configuration please reference forum below. Note your motor is a custom motor made for an OEM you will have to contact machine manufacturer for any specs on it. Also verify if the driver is providing correct A/phase to motor. https://www.orientalmotorforum.com/vie...
by om_tech_support_KR
Wed Feb 26, 2020 2:48 pm
Forum: Stepper Motors and Controls
Topic: PK268-03A stepper motor -DRIVER & CONTROLLER
Replies: 1
Views: 1682

Re: PK268-03A stepper motor -DRIVER & CONTROLLER

Hi jllennard, The compatible unipolar driver CSD2140T has been discontinued a similar bipolar motor and driver combination we offer would be part numbers PKP268D42A2 with connection cables LC2B06E 0.6m or LC2B10E 1m and the driver CVD242BR-K with connection cable set LCS02CVK2. The controller we off...
by om_tech_support_KR
Thu Jan 02, 2020 12:54 pm
Forum: Linear and Rotary Actuators and Controls
Topic: LBE Series, Linear Geared Motor with Control System
Replies: 5
Views: 2768

Re: LBE Series, Linear Geared Motor with Control System

Hi Mr.Thota, For the wiring you can use the internal power of the driver or external power 24 VDC you would choose this with the SW2-1 switch. When ON it uses the built-in power supply of the driver and when OFF you can use an external power supply. Page 35 of the manual shows a wiring diagram when ...
by om_tech_support_KR
Mon Dec 16, 2019 2:04 pm
Forum: Stepper Motors and Controls
Topic: AZ Series - Dynamic speed and Position
Replies: 1
Views: 1805

Re: AZ Series - Dynamic speed and Position

Hi dp1, It is not possible to change the end position or operating speed during an operation you would have to wait until the motor stops to change this. You can have a couple of linked motions without the motor coming to a stop between the 2 operations. Under link you would choose Continuous sequen...
by om_tech_support_KR
Fri Dec 06, 2019 11:09 am
Forum: Stepper Motors and Controls
Topic: Initializing AZ Series Driver
Replies: 1
Views: 1792

Re: Initializing AZ Series Driver

Hi eakirk16, Depending on the driver part number it might have RS-485 Modbus RTU communication. The CC05IF-USB cable isn't necessary for the AZ series just a standard USB mini-B cable to connect to the MEXE02 software. If having difficulties connecting I recommend uninstalling then reinstalling the ...
by om_tech_support_KR
Tue Dec 03, 2019 2:52 pm
Forum: Linear and Rotary Actuators and Controls
Topic: LBE Series, Linear Geared Motor with Control System
Replies: 5
Views: 2768

Re: LBE Series, Linear Geared Motor with Control System

Hi Mr.Thota, The LBE series uses the same driver as the BLE series I will link the manual below and you can reference page 33 for a sample wiring diagram. https://www.orientalmotor.com/products/pdfs/opmanuals/HM-5109-7E.pdf For the external sensors PARP-MS I will link the manual below reference page...
by om_tech_support_KR
Mon Dec 02, 2019 11:33 am
Forum: Linear and Rotary Actuators and Controls
Topic: LBE Series, Linear Geared Motor with Control System
Replies: 5
Views: 2768

Re: LBE Series, Linear Geared Motor with Control System

Hi Mr.Thota, The LBE2F90MC-8-1 package does include a 1 meter connection cable and the external potentiometer PAVR-20KZ. The LXDT-4 part number is only the 4 pieces of limit switch dogs. If you were looking for the sensors also then the part number would be PARP-MS which includes 2 limit switches, 4...