AR-series: home/LS sensors with 48v power supply

Postby vazkus » Fri May 11, 2018 3:17 pm

Hi,
I have a setup with a ARD-KD driver that runs on 48v power supply. I need to connect 1+ inductive sensors (like Bernstein KIB-M12) for home/limit switching. What is the right way of connecting these sensors? Does the driver provide 24v (or anything <36v) that I can use as a VCC for the sensor?

Thank you.

om_tech_support_KR
Posts: 4
Joined: Thu Jan 11, 2018 3:03 pm

Re: AR-series: home/LS sensors with 48v power supply

Postby om_tech_support_KR » Mon May 14, 2018 12:34 pm

Hi Vazkus,

For the ARD-KD the I/O are open collector type so they do not supply any voltage you will have to supply the 24 VDC externally. We do have a sample wiring for the home/limit sensors when using NPN or PNP type reference them below. They can also be found on page 75 and 76 of the manual I will link it below.

http://www.orientalmotor.com/products/p ... 340-2E.pdf

NPN
npn.png
npn.png (130.42 KiB) Viewed 43 times


PNP
pnp.png
pnp.png (130.69 KiB) Viewed 43 times

vazkus
Posts: 4
Joined: Fri May 11, 2018 2:30 pm

Re: AR-series: home/LS sensors with 48v power supply

Postby vazkus » Mon May 14, 2018 2:29 pm

Thank you very much for your quick and prompt response!